If you are going to recommend not using EOL devices on a Normally Open zone shouldnt you explain that if there is a break in the wiring the user will never know unless they test the zone often? For a water zone I would use the EOL since I doubt the user will want to test that often based on its location etc.
No, I am not recommending no supervision. I am recommending omitting the EOL
at first until it is confirmed that the sensor will work with the zone.
The OP has two issues, one is learning how to apply EOL supervision and the other is confirming that the sensor will work on a zone. It is obviously necessary to establish as the first step that the sensor works. This type of sensor is just a few square inches of exposed metal that does not necessarily go closed when immersed, it only drops down to a few kilohms -- maybe not even that low, and maybe/probably not enough to trigger the zone.
Anyway I don't use this type, I have the GRS sensors, both powered and unpowered. With the powered sensors I do use EOL resistors, properly located out at the sensors, at "end of line".