[SIZE=10.5pt]I'm trying to connect a ADT / Elmdene 7422-G3F external sounder to my Omnipro II panel and looking for advice. [/SIZE][SIZE=10.5pt]I've connected 'normal' two wire sounders before, but this has a battery backup and hold off terminals and "comfort LEDs" to warn-off intruders, so needs a [/SIZE]consent[SIZE=10.5pt] power supply. Anyone know the correct & [/SIZE]recommended[SIZE=10.5pt] way to [/SIZE]connect[SIZE=10.5pt] such a sounder to an omnipro II? [/SIZE]
[SIZE=10.5pt]This is as far as I've got, [/SIZE]I've connected:
The Sounder does have a R- terminal which says is the correct way to trigger the sounder, and if I apply Ground to this nothing happens, but if I temporarily apply +12v to it the siren sounds and I can't turn it off again, without temporarily applying 12+ to the Engineers terminal.
Applying Ground to the ST- terminal makes the main alarm strobes come on as expected, and removing the connection makes them go off again.
From the above I could get the omnipro to trigger the sounder by using a relay to temporarily apply 12v to the R- terminal, and temporarily apply 12v to the Engineers terminal to turn it off again. But this doesn't feel very intuitive which makes me think I'm doing something very wrong. Any help gratefully received.
[sharedmedia=gallery:images:1295]
All the best
Dean
[SIZE=10.5pt][/SIZE]
[SIZE=10.5pt]I'm trying to connect a ADT / Elmdene 7422-G3F external sounder to my Omnipro II panel and looking for advice. [/SIZE][SIZE=10.5pt]I've connected 'normal' two wire sounders before, but this has a battery backup and hold off terminals and "comfort LEDs" to warn-off intruders, so needs a [/SIZE]consent[SIZE=10.5pt] power supply. Anyone know the correct & [/SIZE]recommended[SIZE=10.5pt] way to [/SIZE]connect[SIZE=10.5pt] such a sounder to an omnipro II? [/SIZE]
[SIZE=10.5pt]This is as far as I've got, [/SIZE]I've connected:
- [SIZE=10.5pt]the battery to the BATT + & - terminals[/SIZE]
- [SIZE=10.5pt]And constant 12v & Ground to the hold off (H) + & - terminals (which powers the unit and brings on the [/SIZE]
"comfort LEDs")
The Sounder does have a R- terminal which says is the correct way to trigger the sounder, and if I apply Ground to this nothing happens, but if I temporarily apply +12v to it the siren sounds and I can't turn it off again, without temporarily applying 12+ to the Engineers terminal.
Applying Ground to the ST- terminal makes the main alarm strobes come on as expected, and removing the connection makes them go off again.
From the above I could get the omnipro to trigger the sounder by using a relay to temporarily apply 12v to the R- terminal, and temporarily apply 12v to the Engineers terminal to turn it off again. But this doesn't feel very intuitive which makes me think I'm doing something very wrong. Any help gratefully received.