EOL resistors are not optional on all control panels. Many installer put them at the control if the control does not have a EOL disable programming option which makes the EOL useless.
As I stated in other threads with the EOL in place the M1 control has about +- 2 volts of transient noise immunity. With a Normally Closed zone loop the control has about 9 volts of noise immunity. When the zone input uses normally closed loop wiring, the zone is directly connected to the negative side of the power supply, giving additional transient noise immunity.
With the M1 you can program each zone for EOL, normally closed, or normally open.
I use normally closed for residential, but that is my opinion.
Hi Spanky,
This all make sense. What is the transient noise immunity with normally open? I would have thought in lightening prone areas that the normally closed would be the least likely to cause issues. Normally open would have two high impedance transmission lines just be interested in what M1 would make of it given some lightening dancing around.
Cheers,
Fleetz