Came home last night to a zone trouble on one of my CO detectors. its a CO1224 from System Sensor, but was making a beep that is not listed in the manual. It wasnt a temp4 like a valid CO alarm (I even had the fire dept out just to make sure), but it was just a constant beep beep beep beep....with no pauses or pattern.
I finally found the cause: the Altronix power supply it was connected to was NOT showing as connected to AC. The Green led wasnt lit, only the DC LED was lit. There is no explanation for that set in their manual,. I measured 120V at the input, and checked the supervisory contacts and they were both set to fail (A/C fail and battery fail).
Pulled the plug from the wall, plugged back in but no go. Shut everything down (including the PD9 in the Elk box that it powers), unplugged and replugged, no go.
I unplugged the Elk power adapter and re-plugged it in, then did the same for the Altronix and now all of a sudden its back to life.
The only thing out of the ordinary to happen lately was that we lost power 2 weeks ago and were running on generator for a day.
Any ideas?
Thanks.
-Chris
I finally found the cause: the Altronix power supply it was connected to was NOT showing as connected to AC. The Green led wasnt lit, only the DC LED was lit. There is no explanation for that set in their manual,. I measured 120V at the input, and checked the supervisory contacts and they were both set to fail (A/C fail and battery fail).
Pulled the plug from the wall, plugged back in but no go. Shut everything down (including the PD9 in the Elk box that it powers), unplugged and replugged, no go.
I unplugged the Elk power adapter and re-plugged it in, then did the same for the Altronix and now all of a sudden its back to life.
The only thing out of the ordinary to happen lately was that we lost power 2 weeks ago and were running on generator for a day.
Any ideas?
Thanks.
-Chris