AnthonyZ
Active Member
I've recently started graphing temperature data throughout my house, including the thermostat's current temperature value. It's been a great tool to be able to visually note what is happening with my HVAC system and general comfort. Turns out, it's also revealed an issue that I didn't notice before. On a very inconsistent basis, the thermostat is "dropping out" and I am logging a temperature of -40 degrees. The drop is very intermittent. One day it will be stable all day and the next it may drop 2-3 times. Having seen this behavior via the data logging, I have tried to catch the thermostat red handed and I have. Twice, I have been able to get to the 'stat when it drops out (which typically lasts for a few seconds to a minute). What I have noted is that the display is dead but that it's relays are still energized. Meaning that if it's calling for heat when it goes blank, the relay's wiper remains in the same position and the call for heat is maintained. If I pull the face of the 'stat off the wall, of course the circuit is broken and the call for heat is ended. When I place the 'stat back on the wall at that point (at least the two times I've caught it), it fires back up. It's the danged sporadic nature of the problem that makes it more difficult to troubleshoot. My gut is thinking that there is an issue with current draw as that has always been an issue with HAI thermostats but, why then wouldn't it always be a problem? I do have current stealing via the additional common properly wired (this isn't my first rodeo). Anyone else care to chime in and steer me elsewhere before I drop time and money into a larger transformer?